Did you evacuate the system after you opened it? Air is non-condensable and it will cause the pressure to overshoot if left in.

If you didn't pull a vacuum, then you should recover the charge, evacuate and recharge.

How much refrigerant does the system call for and how much did you put in?
Charging by weight gives the best result if you have the patience to do it right.